We are finding that many of the ESM service providers are reporting and failing hydrant system water supplies. After having worked with a number of contractors we provide this process to help those that may think they need to update their water supply when in fact it is not necessary.
Conducting Flow Tests at a Fire Hydrant
Flow tests at a fire hydrant are essential to determine the available pressure and flow, ensuring the fire protection system is adequate. The following steps outline the process and considerations for conducting these tests effectively:
Purpose
The main goal of a flow test is to measure the available pressure and flow at a fire hydrant when the 95% static pressure is provided by the water agency. This data is critical for designing and maintaining fire protection systems.
Procedure
Preparation:
Confirm the static pressure provided by the water agency.
Identify the hydrant to be tested and an adjacent hydrant for pressure reading.
Flow Testing:
Open the selected hydrant fully to allow water to flow.
Use a pitot tube to measure the velocity pressure of the flowing water. The pitot tube should be placed in the stream of water at a right angle to get an accurate reading.
Record the velocity pressure indicated by the pitot tube.
Flow Rate Determination:
Using the recorded velocity pressure, calculate the flow rate. This involves using standard formulas or charts that correlate the velocity pressure to flow rate, taking into account the size of the hydrant outlet.
Pressure Reading:
It is crucial to determine the available pressure at another location, typically an adjacent hydrant, while the initial hydrant is flowing.
Some practitioners neglect this step, resulting in conservative pressure values that may not reflect the true capacity of the system. This can lead to issues, especially if the pressure is near or below acceptable limits.
Data Interpretation:
The pressure reading from the second hydrant should be used to assess the actual available pressure during flow conditions.
Compare this pressure against acceptable limits and design requirements to ensure compliance and reliability of the fire protection system.
Common Pitfalls
Skipping the Secondary Pressure Reading: Failing to take a secondary pressure reading can lead to underestimating the available pressure, potentially compromising the system's effectiveness.
Conservative Reporting: While conservatism in reporting may seem safe, it can be problematic when the pressure is close to or below the required limits, leading to insufficient fire protection.
Conclusion
Flow tests at fire hydrants provide essential data for fire protection system design and maintenance. By ensuring both the flow rate and available pressure are accurately measured and reported, practitioners can avoid conservative estimates that may compromise safety. Always conduct a secondary pressure reading at an adjacent hydrant to obtain a true representation of the available pressure.
------------------------------
Paul Verheijden
------------------------------